    <font face="Times New Roman, Times, serif">Matthew, all,<br>
    </font><font face="Times New Roman, Times, serif"><br>
      AS60038, was published in Australia on 23rd January 2000 to</font><font
      face="Times New Roman, Times, serif"> replace the previous 240V
      standard. This requires</font><font face="Times New Roman, Times,
      serif">, under normal service<br>
      conditions, that the</font><font face="Times New Roman, Times,
      serif"> voltage at the point of supply should not differ from the
      nominal voltage of 230/400V by more than +10%,-6%. <br>
      Voltage drop within a customer's premises may reduce this by
      another 5%, the maximum permissible under AS/NZS 3000, known as
      the Wiring Rules.<br>
      Essential Energy therefore say that the total variation can be as
      wide as +10%, -11%. Essential Energy realises that this voltage
      range may cause issues with 240V equipment and they, therefore,
      have adopted the range of 230V, +10%, -2%, which aligns very
      closely with the old 240V standard. When I was the Supply
      Irregularity Officer with a County Council (not Essential Energy)
      the standard was 240V, ±6%, or 226V-254V. I know that other states
      had different standards at the time, and maybe they still do.<br>
      <br>
      The current Essential Energy "standard" of 230V, +10%, -2%, is
      within AS60038 requirements, and returns a voltage range of
      253V-225V. The AS60038 percentages return 253V-216V. <br>
       <br>
      During my time in the position of SIO the nominal HV supply was
      11,000V, and that tap setting was chosen on distribution
      transformers. Under unloaded network conditions the LV would be at
      near the top allowable figure of 254V, and network load would
      reduce that figure.<br>
      <br>
      Whilst the "nominal" voltage may be 230V according to AS60038, in
      practice, it appears little (nothing?) has changed since the 240V
      standard. <br>
      <br>
      Ray vk2tv<br>
      <br>
      <br>
      <br>
      <br>
    </font>
    <div class="moz-cite-prefix">On 17/02/16 21:30, Malcolm Larkin
      wrote:
      <pre wrap="">We haven't had 240V AC in Australia since the 23rd of January 2000. The day we dropped to 230V</pre>
    </div>
    <font face="Times New Roman, Times, serif">It is allowed to be +5% /
      -10% (241.5 to 207)
      Previously when 240, it was ± 10% so 264 to 216<br>
    </font><br>
    <br>
    <br>
    <blockquote
      cite="mid:17CB3513-7CD5-4262-87D9-EDA7ED604F4D@icloud.com"
      type="cite">
      <pre wrap="">

Sent from my iPhone

</pre>
      <blockquote type="cite">
        <pre wrap="">On 17 Feb 2016, at 18:56, Liz VK2XSE <a class="moz-txt-link-rfc2396E" href="mailto:edodd55@gmail.com"><edodd55@gmail.com></a> wrote:

QTR Wed, 17 Feb 2016 09:41:42 +1030 Matthew Cook QTC

</pre>
        <blockquote type="cite">
          <pre wrap="">It's better your iGate sips and not sucks on the 240VAC regardless
these days o_O

73

Matthew
VK5ZM
</pre>
        </blockquote>
        <pre wrap="">


Mine is solar powered - radio and the computer setup
The planned one is for a place where the power is provided by my son's
employer at very good rates ;)


-+-+-+-+-+-+-+-+-+-+-+
Liz
VK2XSE
_______________________________________________
OZAPRS mailing list
<a class="moz-txt-link-abbreviated" href="mailto:OZAPRS@aprs.net.au">OZAPRS@aprs.net.au</a>
<a class="moz-txt-link-freetext" href="http://lists.aprs.net.au/mailman/listinfo/ozaprs">http://lists.aprs.net.au/mailman/listinfo/ozaprs</a>
</pre>
      </blockquote>
      <pre wrap="">_______________________________________________
OZAPRS mailing list
<a class="moz-txt-link-abbreviated" href="mailto:OZAPRS@aprs.net.au">OZAPRS@aprs.net.au</a>
<a class="moz-txt-link-freetext" href="http://lists.aprs.net.au/mailman/listinfo/ozaprs">http://lists.aprs.net.au/mailman/listinfo/ozaprs</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>