I use a big hooa diode, about 80A and have this between my 200AH of
batteries and the power supply.

Load is connected to the battery side of the diode and the power supply is
wound up to 14.6V to cater for the 0.8V drop of the diode.

Automatic and simple.


Regards,
Gordo VK4VP

-----Original Message-----
From: ozaprs-bounces at aprs.net.au [mailto:ozaprs-bounces at aprs.net.au] On
Behalf Of Andrew Rich
Sent: Sunday, 4 November 2007 6:15 PM
To: ozaprs
Subject: [OZAPRS] Power supply options

Just got myself setup with a 13.8 40A Switchmode PSU.

I am keen to hear what backup power supply options people are running ?

I have a rather large SLA battery here.

I am trying to avoid a relay switched solution.

Perhaps a UPS on the front end of the power supply might be an option ?

I also have a trickle solar charger and reg.

--------------------------------------------------------------------------
--
Andrew Rich VK4TEC